There is no justification for omitting sprinklers in that room regardless of what type of system lies beside it.
Craig L. Prahl Fire Protection Group Lead CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29303 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Friday, August 28, 2015 4:10 PM To: [email protected] Subject: Clean room sprinklers We have a building with a ESFR sprinkler system installed that the owner has decided to install a portable clean room in. The room itself has plastic sheeting for walls and the ceiling is composed of air vents and acrylic panels. No storage of combustibles is allowed inside and they use it to check LED panels for defects. The room is about 12X20. Is there any exception in NFPA 13 that would allow the omission of sprinklers from the room? It just seems silly to require sprinklers in the room when you have 30ft rack storage next to it protected by the ESFR system. Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org