There is no justification for omitting sprinklers in that room regardless of 
what type of system lies beside it.

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Friday, August 28, 2015 4:10 PM
To: [email protected]
Subject: Clean room sprinklers

We have a building with a ESFR sprinkler system installed that the owner has 
decided to install a portable clean room in.  The room itself has plastic 
sheeting for walls  and the ceiling is composed of air vents and acrylic 
panels.  No storage of combustibles is allowed inside and they use it to check 
LED panels for defects.  The room is about 12X20.  Is there any exception in 
NFPA 13 that would allow the omission of sprinklers from the room?  It just 
seems silly to require sprinklers in the room when you have 30ft rack storage 
next to it protected by the ESFR system.

Thanks,

Dewayne