Does anyone have any knowledge on installing concealed pendent sprinklers in
false beams? The Reliable cut sheet (bulletin 006 Rev I) for RFC43 says “top
of deflector to ceiling installed in beams ½” to 1”. Now the residential
sprinkler design guide (bulletin 140 Rev K)  specifically says “RFC
concealed sprinklers cannot be installed in structural or false beams that
impede the flow of air through the vent holes into the space above.”  I’m
not exactly sure what would impede the flow???

 

The Tyco cut sheet  only says the deflector to ceiling for concealed heads
installed in beams  7/8” to 1 1/8” below bottom of beam. When I called Tyco
all the guy said was, from the way we understand it you can install them in
beams and just follow NFPA sprinkler deflector criteria…….he didn’t sound
very convincing and I’m just all around confused, I do very little
residential project so I’m not as familiar and up to date on all things
residential.   Any information would be helpful. 

 

Thank You  

 

Rocci Cetani III, CET

Lead Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

[email protected]

www.norcalfire.com <http://www.norcalfire.com/> 

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to