I would say you can calc your system back to the gauge on the riser only when 
you have completed a flow test where the effective point of the test is the 
gauge on the riser.  E.g., you have a backflow test connection that ties to the 
riser at or near the point of connection of the gauge.

Otherwise, I could have a riser with a gauge that reads 50 psi.  I look down 
and follow the 4" pipe to the ground and it disappears.  For all I know that 4" 
ties into a 75 year old 6" coast iron pipe that has deteriorated to the point 
that it is effectively a 2" diameter pipe.  The flows available through that 6" 
pipe are miniscule compared to a new 6" with a c-factor of 140 or 150.  Yet I 
still have a static pressure on the riser of 50 psi. The point being, as Craig 
said, we don't know anything about the water supply to that riser by simply 
reading the static pressure on that gauge.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Sean Lockyer
Sent: Tuesday, October 20, 2015 5:24 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Is calcing back to the riser gauge acceptable ?

Quick question for everyone here. When the situation prevents one from being 
able to provide a calculation back to the U.G. connection at the street when 
can you calculate the system back to the gauge on the riser ?

For example, if you have, say, 50 psi city pressure (worst case) on a system at 
the riser gauge couldn't one calc it to the base of the riser, add in your hose 
allowance and call it a day as long as your system demand is less than the 
lowest "day pressure" in the system ?

In addition, if there any mention on this in NFPA 13 ?


              Sean Lockyer
              Project Designer                               4617 Parkbreeze 
Court
              Cell    386-279-1197                              Orlando, 
Florida 32808
              slock...@aitlifesafety.com              Phone:      407-816-9101
              www.AITLifeSafety.com                       Fax:         
407-816-9104


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to