Rocci,
I completely agree with Greg. I would add the reference to item 3 in the section of the standard, 11.2.3.2.3.1, which specifically uses the word "ceiling", not "roof." When it comes right down to it, you can point right to that paragraph, and ask the AHJ to show you where he found the reference in -13 to support his position. In short, "prove it."
good luck,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 11/10/2015 12:24 PM, Greg McGahan wrote:
He is incorrect unless the ceiling is open enough to count the roof deck as
part of the same space. The table states "ceiling height".

Respectfully,



Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852

On Tue, Nov 10, 2015 at 2:19 PM, Rocci Cetani 3 <[email protected]>
wrote:

I have an AHJ claiming that because the roof deck is 18' I can't use the
40%
quick response reduction even though a ceiling is being installed at 9'
AFF.
I have never been questioned on my approach it seems pretty straight
forward..Is he correct in stating I should base my reduction on the 18'
roof
deck?



Thanks in advance for your input



Rocci Cetani III, CET

Lead Designer

Water-Based Fire Protections Systems Layout, Nicet Level III



Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590





[email protected]

www.norcalfire.com <http://www.norcalfire.com/>



CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking
of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.



_______________________________________________
Sprinklerforum mailing list
[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to