There's not really a "brewery" section in the codes and standards but you're 
dealing with very low alcohol-content liquids on the beer side, so brewing and 
storage are likely ordinary hazard there.  And a restaurant is what it is.  The 
issue is the still and how much high-test will be produced; we did a 
micro-distiller here in San Diego County who has one still but it's of a size 
that will produce about 100 gallons at a time of nearly pure grain alcohol and 
that required special attention as a Class IA flammable/combustible liquid.  I 
would definitely look at it from the FCL and haz-mat perspective or bring in a 
code consultant with some experience.  Even with sprinklers, you may find 
yourself needing separate fire control areas for the distilled spirits ...

SL





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Mote
Sent: Thursday, November 19, 2015 1:25 PM
To: [email protected]
Subject: Brewery and Still Works

Can anyone point me in the right direction regarding the correct hazard for 
sprinklers in an approximately 6000 sq. ft. 2 story + basement, Brewery / Still 
Works / Pub / Restaurant. I have looked through IBC 2009 and found nothing , 
NFPA 13, 2007 says distilleries are Ordinary Group II. I'm thinking that may 
not be adequate for some of the areas. In our kick off meeting they were 
discussing explosion proof lighting and switches in the approx. 677 sq. ft. 
bonded storage room, and the 630 sq. ft. Distillery area. Anyone have any 
thoughts?

Richard L. Mote CET
Design Manager
Rowe Sprinkler Systems, Inc.
P 570-837-7647 or 877-324-ROWE
F 570-837-6335
[email protected]

*** Confidentiality Notice ***
This email and any attachments thereto may contain information that is 
privileged and confidential and is intended only for the use of the addressee. 
If the reader of the message is not the intended recipient or an authorized 
representative of the intended recipient, you are hereby notified that any 
dissemination of this communication is strictly prohibited. If you have 
received this communication in error, please notify us immediately by e-mail at 
[email protected] or by telephone at 570-837-7647 and delete the 
message and any attachments permanently from your system.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to