It is covered by 13 and it is excessive (especially having to retain a k-5.6) but you’ll still have to include all in the calc. When using the full design area (no reductions for QR etc so 1500 sf for LH wet and 1950 for LH Dry etc) you can omit form the calculation sprinklers in closets and similar small rooms. You can omit including the sprinkler under obstructions and calc just the one at the ceiling (but it is considered to have 2 sprinklers covering the same floor area). Although the area of coverage is very small and your overage is VERY high, you still have to include all sprinklers within the remote area except as identified above.
Your only prayer is the AHJ providing an allowance due to the unique of the situation combined with them requiring a minimum K-5.6. Good luck. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Jan 5, 2016, at 9:32 AM, Art Tiroly <[email protected]> wrote: > > We have a discussion about sidewall and pendant sprinklers in a 36" x 16" > soffit that surrounds a dorm rooms in a jail. > > Do the QR pendant sprinklers need to be calculated with the QR sidewall > sprinklers in the 900 SF area? We have 14 sprinklers flowing in areas that > seems excessive and not required. Can't find where this covered in 13. > > Appreciate your help. > > Art Tiroly > ATCO Fire Protection/Tiroly > 24400 Highland Rd CLE 44143 > 216-621-8899 > 216-570-7030 cell > > > > > > > --- > This email has been checked for viruses by Avast antivirus software. > https://www.avast.com/antivirus > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org