You have a good memory Roland. I submitted Public Input 289 for the "S" dimension off the wall to be corrected to be "½S" and for the "18 in. minimum (No Maximum)" to be revised to "No Maximum" and that was accepted by the Committee and published in the 1st Draft Report.
Somehow though, when the 2nd Draft Report came out, those changes were lost and the original unrevised illustrations were back in there. I notified Matt at NFPA about this, but he wasn't able to get it fixed - procedural limitations I guess. I believe that in NFPA 13-2016 Figures 8.6.5.1.2(c) and 8.8.5.1.2(c) and 8.10.6.1.2(c) were meant to be similar to the new Figures 8.9.5.1.4(c) and 8.10.7.1.4(c). Maybe we can get it fixed during the next cycle. There should probably be a new figure for Section 8.7 as well. Larry Keeping -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Roland Huggins Sent: January-21-16 2:06 PM To: [email protected] Subject: Re: NFPA 13, 2013; figure 8.6.5.1.2(c) what confused the issue is that you attempted to start a new thread by replying to a thread on trailers within a warehouse. This is a goofy item that defies logic. There was something in the FR and/or SR reports on this where I thought the 18 inch minimum went away (which then is logical). Will look into AFTER I finish an overdue article (unless you beat me to it and tell us - lol) Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Jan 21, 2016, at 9:47 AM, T. Silva <[email protected]> wrote: > > Trying to understand the logic of this section. If the height from deflector > to bottom of obstruction is 18" or over it is not an obstruction, but if the > height is less than 18" then it is? > > This section is also in the 2016 edition. > > Tony _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org