Does 8.15.1.2.18 work for you? Exterior soffits, eaves, overhangs, and 
decorative frame elements.

Tom Wellen

> On Jan 22, 2016, at 8:41 AM, Michael Hill <[email protected]> wrote:
> 
> Most of the holes that I have seen for dormers are cut between joists, not
> the full opening, and most of the dormers are more than 36" tall. The
> plywood would create combustible construction as well, that would eliminate
> ceiling pocket exclusion as an option. I guess if the type of construction
> worked out and you met the other requirements, you could try to classify it
> as a ceiling pocket. I think it would be an uphill battle with the AHJs in
> our area, but might be worth a try.
> 
> Mike Hill
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of Brad Casterline
> Sent: Friday, January 22, 2016 9:33 AM
> To: [email protected]
> Subject: RE: Roof dormer sprinklers?
> 
> If the hole cut in the plywood was the footprint of the dormer it would not
> be a concealed space. Then, if the dormer dimensions played ball, could it
> be a ceiling pocket not requiring sprinklers?
> 
> Brad
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of Michael Hill
> Sent: Friday, January 22, 2016 7:53 AM
> To: [email protected]
> Subject: RE: Roof dormer sprinklers?
> 
> I think it still falls under combustible concealed space and needs
> sprinklers. Everyone that I have run across ended up having a hole cut in
> the plywood for access to the dormer.
> 
> Mike Hill
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of [email protected]
> Sent: Friday, January 22, 2016 8:24 AM
> To: sprinklerforum <[email protected]>
> Subject: Roof dormer sprinklers?
> 
> I have an attic with decorative roof dormers built above the roof and
> separated from the attic space below by plywood sheathing.  Do I need to
> poke heads up into the dormers? I have been doing this in the past, but now
> am wondering if it is necessary. 
> 
> 
> 
> Bill Menster
> WFM Consulting Inc. 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org