Right now all the various commentary including manufacturer MSDS and PSDS says water as the primary means for fire control. The FM Global 2013 white paper recommended using design criteria for Cartoned Unexpanded Plastic storage. The array of shapes, sizes and other characteristics of new battery technology creates a daunting task for researchers in trying to determine design criteria for all the possible combinations and configurations and chemical properties involved with Lithium based battery technology.
While dry chem is one recommended means for some level of control on a small scale, dry chem cannot guarantee extinguishment. Also if the enclosure is opened, reignition could occur as the concentration level of agent drops within the space. Protecting a large space with Dry Chem also poses logistical challenges. Water will provide cooling and can reduce or control thermal runaway produced by adjacent batteries. Exposure to temperatures over 400 deg (F) for Li-On batteries can initiate a runaway condition, for Li-Po batteries the temperature is less. One caution in using water is that hydrogen gas can be liberated from the burning batteries. So a healthy water supply should be provided for initial sprinkler flow as well as for the ground attack that would need to be initiated. There is one company I found that uses an argon based foam system for aircraft storage bays as a suppression agent for lithium batteries. Not sure if that system could be employed in a warehousing configuration. Craig L. Prahl Fire Protection Group Lead/SME CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29303 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of å... .... Sent: Friday, February 26, 2016 3:35 AM To: [email protected] Subject: Re: Lithium battery storage Dry chem would be a messy clean up, but probably the best agent for suppression, if a medium- to high-expansion foam (including CAF) with dry-chem together are not the top suppression agent for reasons of: suppression effectiveness cleanup ease minimal amount of agent The advantage of the medium- to high-expansion foam is some effective suppression of toxic vapors while emergency response team is at fire's peak exposure times. The foam also 'sticks' where 'gaseous' agents have issues with open doors, HVAC, unrepaired holes in walls and in raised floor conduit spaces, and egress requirements for personnel due to either toxicity or hypoxia. Scot Deal Excelsior Risk/Fire Engineering _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org