Right now all the various commentary including manufacturer MSDS and PSDS says 
water as the primary means for fire control. The FM Global 2013 white paper 
recommended using design criteria for Cartoned Unexpanded Plastic storage.  The 
array of shapes, sizes and other characteristics of new battery technology 
creates a daunting task for researchers in trying to determine design criteria 
for all the possible combinations and configurations and chemical properties 
involved with Lithium based battery technology.

While dry chem is one recommended means for some level of control on a small 
scale, dry chem cannot guarantee extinguishment.  Also if the enclosure is 
opened, reignition could occur as the concentration level of agent drops within 
the space.  Protecting a large space with Dry Chem also poses logistical 
challenges.

Water will provide cooling and can reduce or control thermal runaway produced 
by adjacent batteries.   Exposure to temperatures over 400 deg (F) for Li-On 
batteries can initiate a runaway condition, for Li-Po batteries the temperature 
is less.  One caution in using water is that hydrogen gas can be liberated from 
the burning batteries.  So a healthy water supply should be provided for 
initial sprinkler flow as well as for the ground attack that would need to be 
initiated.

There is one company I found that uses an argon based foam system for aircraft 
storage bays as a suppression agent for lithium batteries.  Not sure if that 
system could be employed in a warehousing configuration.  



Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of å... ....
Sent: Friday, February 26, 2016 3:35 AM
To: [email protected]
Subject: Re: Lithium battery storage

Dry chem would be a messy clean up, but probably the best agent for 
suppression, if a medium- to high-expansion foam (including CAF) with dry-chem 
together are not the top suppression agent for reasons of:
  suppression effectiveness
  cleanup ease
  minimal amount of agent

The advantage of the medium- to high-expansion foam is some effective 
suppression of toxic vapors while emergency response team is at fire's peak 
exposure times.  The foam also 'sticks'  where 'gaseous' agents have issues 
with open doors, HVAC, unrepaired holes in walls and in raised floor conduit 
spaces, and egress requirements for personnel due to either toxicity or hypoxia.


Scot Deal
Excelsior Risk/Fire Engineering
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to