You really should contact 3M and their fire protection division is providing 
direction on protection, many seminars.  I can give you contact information, 
but it might be best to have an FPE involved.

Scott

Office: (763) 425-1001 x 202
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Friday, February 26, 2016 8:57 AM
To: [email protected]
Subject: RE: Lithium battery storage

You have to look at a consensus amongst data, not just one MSDS or not just one 
study.  

In this particular case there are no absolutes, no guarantees of any results.  
Take the info provided and use that to make your best case for a methodology.



Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of å... ....
Sent: Friday, February 26, 2016 9:52 AM
To: [email protected]
Subject: Lithium battery storage

Do we realize who writes those MSDS ?   Although MSDS content has gotten
better over the years... just saying think about the quality of analyses in 
some of those MSDS's.

This commodity is non-standardized territory.
If ecological considerations are a factor, then dump loads of water warrants a 
second look.

We might be able to guarantee control of a Li-battery fire with lots of water, 
but until we get *LOTS* of water, we can't guarantee extinguishment using water 
only, either.

The engineers at Boeing probably have some experience with suppressing
Li-battery fires.   Even though 'in safety there should be no secrets...'
 tell that to the economists.


Scot Deal
Excelsior Risk/Fire Engineering
Scot Deal
Excelsior Risk/Fire En
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org