That table is for water miscible liquids.  So you better be sure that ALL of 
the liquids stored are water miscible.  I'd be surprised if that was the case.  

Have you worked through the applicable decision tree, probably 16.4.1(b)?

Plastics will generate worst case but if the Class IB is in metal you also need 
to reconcile that hazard then design to the worst case.  

A 0.45 or even a 0.60 gpm/sf density for some materials is not unusual 
especially when dealing with non-miscibles.  Even with miscible liquids the 
amount of water needed to dilute it to a point where it can be considered a 
lesser hazard can be extremely high.   

I'd also ask if they plan to store empty plastic drums in this area as that can 
add another factor to the mix.  

If you just hit a brick wall I'd suggest looking to the FM Global Data sheets 
for additional guidance in dealing with flammable/combustible storage 
protection criteria.


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of David Bitton
Sent: Friday, February 26, 2016 12:32 PM
To: [email protected]
Subject: Liquid Storage Room

Hello,

 

I have a flammable liquid storage room , with an area of less than 500 square 
feet, that  will be used for the storage and dispensing of Class IB, IC, II, 
and IIIA liquids in drums on racks.  The drums will be on side, with two 
storage levels to a height of roughly 6 ft.  Some of the drums will be plastic. 
 In trying to determine the protection criteria from NFPA 30, I keep ending up 
at Table 16.5.2.7, which requires a ceiling density of 0.45/entire area, plus 
horizontal barriers, plus 2 levels of in-racks.  This appears excessive.  Are 
there any other options? 

 

I seem to recall that we could protect a liquid storage room (having an area of 
less than 500 sq. ft.) with a density of 0.60/entire room, regardless of the 
type of drums.

 

David Bitton, ing.

Les services de prévention des sinistres Quest inc.

Quest Loss Control Services Inc.

5100, rue de la Savane, bureau 200

Montréal, QC H4P 1T8

(514) 341-4545

www.questlosscontrol.com

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to