Subject: Pumps shall not be started more than 2 times in 10 hours

For DoD projects there is this requirement in their standard specs:

"The fire pumps shall be operated for a period of at least 10 minutes for each 
of the starts; except that electric motors over 200 horsepower shall be 
operated for at least 15 minutes and shall not be started more than 2 times in 
10 hours."

Anyone know where this comes from and if there is a real concern with starting 
pumps more often than that?  The pumps in this case are 500 hp if that makes a 
difference.   With 10 starts and stops automatically and 10 manually it'll take 
a week to do pump acceptance testing.