http://buildingcoderesourcelibrary.com/Fire_Protection_History.aspx

scroll about 2/3 the way down to Part 211: 1899 (Sprinkler System
Installation Rules)

The earliest Systems were installed based on British Standard Rules and,
even today, the British pipe schedules are more 'lenient' than American
schedules.

I know Roland told me next time I tried to figure out where the max 32
ft/sec came from to take a hammer and smash my thumb instead... I think the
British increased pipe size when the velocity got to 32 ft/s, and the
Americans increased pipe size when it got to 20 ft/s.

OUCH, Brad 




-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Matthew J Willis
Sent: Wednesday, March 16, 2016 7:46 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Old pipe schedule

Ah.., but the crux is, Are you working there under 25 or 13?

R/
Matt

Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.
*NEW ADDRESS*
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108





-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Art Tiroly
Sent: Wednesday, March 16, 2016 6:25 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Old pipe schedule

What is the sprinkler spacing?
Staggered spacing was quite common before 1940.
Newer heads installed?
High pressure water supply connected?
It likely will barely do .10 density or maybe .15 with moderate pressure.
FM used to allow 3-5 psi at end head for pipe schedule.

Art Tiroly
ATCO Fire Protection

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Wednesday, March 16, 2016 7:22 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Old pipe schedule

I am working on a project in a mill that was constructed in 1884. On the top
floor, the branch piping is 3/4 - 1 - 1. Was there an older version of pipe
schedule that allowed smaller pipe or is this just undersized? 
Hopefully some of you history buffs (or at least those with a bunch of old
stuff) would know.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to