First thing, when referencing tables or chapters/sections, please provide the 
year edition and name of the document you're referencing.  I'm assuming NFPA 30.

OH 3 is like 0.195 gpm/sf over 2000 sf area.  That's not suitable for any type 
of appreciable combustible liquid storage.  So that may be a problem.  Also you 
need to know the characteristics of the material being stored.  Much in the 
Class IIIB family tend to be hydrocarbons (non-miscible) and water only 
sprinklers have limited effect on pool fires of those types of materials.   
Know the material being stored, ask for SDS.

You also need to know the container types, metal, plastic or other and will 
there be storage of empty containers?

You didn't state the total quantity to be stored. 

How will the material be stored, on floor, on racks, stacked?

Yes, with sprinklers per Table 9.6.1 there is no upper limit, but for a 
non-sprinklered bldg. you can only have 13,200 gallons per CONTROL AREA and now 
you're getting into building code segregated and size limited areas within the 
bldg.


Table 12.6.2 is for UNPROTECTED as in non-sprinklered.  For a non-sprinklered 
whse you have limits.

You also need to be looking at local building codes for additional requirements 
related to the storage and handling of combustible and flammable liquids.

 

Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Crawford
Sent: Wednesday, March 30, 2016 1:15 PM
To: [email protected]
Subject: Class IIIB Liquid Storage

A client has a building that is protected with an Ordinary Hazard Group 3 
system.

 

They want to store class IIIB combustible liquids in 16 gal and 55 gal drums.

 

Table 9.6.1 gives the MAQ for a IIIB as 13,200 gal with note 1 & 4 and note
4 states that the quantities are not limited if the building is equipped with 
an automatic sprinkler system installed in accordance with NFPA #13.
This seems to imply that they could store an unlimited amount of class IIIB 
liquids.

 

Table 12.6.2.2 gives the MAQ as 55,000 gal if the building is protected with a 
sprinkler system designed for class 4 commodities to 20'.

 

Am I missing something

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  [email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to