My Thursday afternoon ramble.  NFPA 13 (2013) - Table 17.3.3.1: why is there no 
outline for 22.4k @ 35ft storage w/40ft roof?

22k's are defined for 40ft/45ft, 35ft/45ft, 30ft/45ft, 30ft/40ft, and 
30ft/35ft.  All of which have an operating pressure of 40psi except the 35ft 
roof height which is 35psi.  Other than that, I can't seem to find a difference 
between any of them.  I would like to say I can safely assume the design for my 
35ft@40ft building will be 40psi.  Based on the fact that all the other 
surrounding storage height, roof height, and storage to roof clearances all say 
40psi will work.  Also, I back checked 16.3.3.1 which I have found typically 
mirrors the cartoned non-expanded plastics section of 17.3.3.1, and that 
section does have the  35ft/40ft described as 40psi.  I checked 2007 and 2016 
versions and they have this same missing definition.

So what gives?  And if your argument is just "they left it out because the 
35ft/45ft roof covers it".  Then I say "that's fine and dandy, but then why do 
they specifically spell out 30ft/45ft and 30ft/40ft when they are exactly the 
same protection".  I hope I'm missing something or this was just an oversight 
and not just a matter of trying to save ink on the page.