Ahmed,

There aren’t any requirements for temporary warehouses.  The requirements are 
the same as for permanent warehouses.

If a fire starts the fire reacts the same.

You have to protect for the hazards present regardless of the life expectancy 
of the building.

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Nadeem Ahmed
Sent: Saturday, June 18, 2016 6:00 AM
To: [email protected]
Subject: Type of fire protection required for the temporary warehouse - storage 
of Class I, II & IV commodities in a

Dear Gentlemen,

Can somebody advise for the type of fire protection required for the temporary 
warehouse where Class I, II & IV commodities, cables, insulations, small 
quantity of Paints, tools and etc are stored.

Warehouse height is around 11 meters and half portion with single racks and 
other half material are stored on the floor.

This temporary warehouse will be there for one or two years and later it will 
be demolished.

NFPA references if any......


--
Regards

Ahmed