>From the IBC (2012):

[F] 903.3.5 Water supplies.
Water supplies for automatic sprinkler systems shall comply with this section 
and the standards referenced in Section 
903.3.1.<javascript:Next('./icod_ibc_2012_9_par053.htm');> The potable water 
supply shall be protected against backflow in accordance with the requirements 
of this section and the International Plumbing Code.

Duane Johnson, PE
Design Manager
Strickland Fire Protection
4011 Penn Belt Place
Forestville, MD 20747
301-474-1136 Office
301-455-0010 Cell


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bobby Dewar
Sent: Thursday, June 23, 2016 12:10 PM
To: [email protected]
Subject: RE: Two Backflows

>From the Florida Plumbing Code:

608.16.4 Connections to automatic fire sprinkler systems and standpipe systems.
The potable water supply to automatic fire sprinkler and standpipe systems 
shall be protected against backflow by a double check backflow prevention 
assembly, a double check fire protection backflow prevention assembly or a 
reduced pressure principle fire protection backflow prevention assembly.

Exceptions:

1. Where systems are installed as a portion of the water distribution system in 
accordance with the requirements of this code and are not provided with a fire 
department connection, isolation of the water supply system shall not be 
required.

2. Isolation of the water distribution system is not required for deluge, 
preaction or dry pipe systems.


Bobby Dewar, P.E.
Contract Design Manager

Wayne Automatic Fire Sprinklers, Inc.
222 Capitol Court
Ocoee, FL  34761

407-877-5578 - Office
407-656-8026 - Fax
407-721-3762 - Cell
[Description: Description: Description: 
cid:[email protected]]
www.waynefire.com<http://www.waynefire.com/>
We're hiring great people at all of our locations!  Please check out our 
website for the details!

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Irwin
Sent: Thursday, June 23, 2016 12:01 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Two Backflows

This answer I like. Time to dig in to AWWA.

Thanks





John Irwin
Critical System Solutions Sprinkler Construction Manager
813-618-2781<tel:813-618-2781> 
[email protected]<mailto:[email protected]>


Sent from a mobile device. Please forgive brevity, spelling errors and 
punctuation gaffes.


-------- Original message --------
From: [email protected]<mailto:[email protected]>
Date: 06/23/2016 11:57 AM (GMT-05:00)
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Two Backflows
The AWWA has requirements for Backflow Prevention and Cross Connection 
mitigation which are followed by the water purveyors.

It sounds like you have a deficiency and coordination issue in the plans you 
were given.

I would be drafting an RFI to the GC asking them to contact the EOR for 
clarification on the design.

You cannot leave the potable unprotected by not having a backflow on the 
sprinkler connection to the potable.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Irwin
Sent: Thursday, June 23, 2016 11:47 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Two Backflows

Yes I understand what I should do, but it's not my place to go around the 
general contractor, engineer, owner and architect. Only to advise. We have an 
approved site plan and I have an approved sprinkler shop drawing. If viewed at 
the same time the issue becomes apparent. When viewed and permitted separately 
by different entities inside the AHJ office, the trouble is less visible. 
Asking about it would most likely trigger the requirement. And while I think we 
should have a backflow, without a code or ordinance to back me up ... there 
isn't much I can do.

John Irwin
Sprinkler Construction Manager
Critical System Solutions, LLC
Cell:     813.618.2781
Email:  
[email protected]<mailto:[email protected]>


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]<mailto:[email protected]>
Sent: Thursday, June 23, 2016 11:41 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Two Backflows

Fire Sprinkler systems are served off of domestic potable water lines all over 
the place.  Very common.

Your requirement to protect the potable water is coming from the local water 
purveyor or health department not from NFPA 13.  This protection of the potable 
system has been around for decades.

You should be contacting the local water department to find out what type of 
backflow device they require and get direction from them.  That's your first 
stop in this matter.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Irwin
Sent: Thursday, June 23, 2016 11:16 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Two Backflows

I use RPZ as a generic term.

Also I am going under the assumption that I MUST separate my sprinkler from the 
domestic at the point of connection. However it was brought to my attention 
that this may not be required in NFPA anyway. While the thought of sprinkler 
water and domestic water sickens me a bit ... can someone show me where NFPA 
says I must separate them with a backflow?

John Irwin
Sprinkler Construction Manager
Critical System Solutions, LLC
Cell:     813.618.2781
Email:  
[email protected]<mailto:[email protected]>


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Thursday, June 23, 2016 11:07 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Two Backflows

I don't think there's any prohibition and we've been asked to do this before.  
I would check with serving water and fire departments to be sure that both 
devices satisfy the requirement of their respective masters.  RPZ's are not UL 
classified for fire service and usually configured with non-indicating valves 
for general water service.   NFPA standards require ALL valves controlling fire 
protection water supplies to be LISTED (for fire service) indicating type and 
building code requires them to be supervised.  Have fun ...

Steve

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Irwin
Sent: Thursday, June 23, 2016 8:03 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Two Backflows

I am working on a project where the developer and site contractor have decided 
that fire and domestic should share an underground line around the site and to 
the building. At the street there is a meter assembly and a Wilkins 375A RPZ. I 
would need to install an additional backflow at my point of connection because 
the line is shared all the way to the water room. Other than being a dumb way 
to do this and having two pressure losses in my calculations, is there any code 
that says I can't gave two RPZs in my water line?


John Irwin
Sprinkler Construction Manager

Critical System Solutions, LLC
2830 Scherer Drive, Suite 300
St. Petersburg, FL  33716
Office: 727.209.5122
Fax:      727.209.5126
Cell:     813.618.2781
Email:  
[email protected]<mailto:[email protected]>