2014 NFPA 25 14.3.1 (12) requires an obstruction investigation, it isn’t a 
maybe, it is a shall.

Scott

Office: (763) 425-1001 x 202
Cell: (612) 759-5556

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Forest Wilson
Sent: Wednesday, July 06, 2016 10:30 AM
To: [email protected]; [email protected]
Subject: Re: Sodium Silicate


I encountered a similar situation a few years ago. I would send a letter to the 
ahj and owner explaining what you found and notify them the system may be 
impaired.
Suggest lab testing to confirm if needed and then ask the ahj for guidance.
On Jun 16, 2016 8:21 PM, "Jeff Bridges" 
<[email protected]<mailto:[email protected]>> wrote:
We found some- actually quite a bit, of sodium silicate, in the FDC drop above 
the check valve (about 3” thick 4” diameter).
The FDC is located off the end of the feed main side of a gridded system.
This is after doing a 100 head TI where we didn’t see anything unusual from the 
branch piping.
NFPA 25 Annex D.5 directs a flushing of the entire system.
Am I correct?