NFPA 13 is different from 13R in that 13R requires up to the four most 
demanding sprinklers within a compartment, but 13 requires the four most 
demanding sprinklers which may or may not be within the same compartment.  When 
doing multi-family projects that fall under 13, I typically wind up calculating 
all of the sprinklers within the living/kitchen areas and a bedroom (or two) 
depending on what it takes to reach the required four heads.  I’ve never taken 
the calculation for a unit beyond the unit.  But then I normally do a separate 
calculation for the corridors, too.

[CFP LOGO2]
Curtis Tower | Project Design Manager
10550 Olympic Drive, Dallas, TX 75220
Office: (214)496-9797 | Cell: (682) 667-0323 | Fax: (214)496-9201
[email protected]<mailto:[email protected]> | 
http://www.centralfireprotection.net/
Central Fire Protection | Since 1982 | Dedicated People | Powerful 
Protection<http://www.centralfireprotection.net/>

From: Steve Leyton [mailto:[email protected]]
Sent: Wednesday, July 06, 2016 2:04 PM
To: [email protected]
Subject: RE: Dwelling Unit Sprinkler Calc

What state is that?   In CA, you have to have one-hour between dwelling units.

SL

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Wednesday, July 06, 2016 11:49 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Dwelling Unit Sprinkler Calc

I would watch out on this.  I am designing a high rise right now that the 
builder states the only fire rated walls per floor are the common corridor 
walls.  I asked if the walls between the units will be rated and he said no.

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Roland Huggins
Sent: Wednesday, July 06, 2016 12:55 PM
To: [email protected]<mailto:[email protected]>; 
[email protected]<mailto:[email protected]>
Subject: Re: Dwelling Unit Sprinkler Calc

I’d look at whether it qualifies for the room design method (since dwellings 
units are separated by fire rated construction but the protection of openings 
poses a question).


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org<http://www.firesprinkler.org/>



On Jul 5, 2016, at 12:34 PM, Bob 
<[email protected]<mailto:[email protected]>> wrote:

I have a NFPA 13 building with Dwelling Units.  They each have three 
Residential Sprinklers.  13 requires a four head calc.  Can I calc the 3 
residential sprinklers and pick up one QR sprinkler in the corridor and still 
satisfy the 4 head requirement?  Or, should I pick up one residential sprinkler 
from an adjacent dwelling room?

Thank you,

Bob Knight, CET III
208-318-3057
[cid:[email protected]]

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to