Conservative but not unheard of.  One of the most common bad practices is to 
make up a bunch of pre-cut drops and clue them into branch outlets 
assembly-line style.  If done in a hurry with too much cement, you get runs 
that can wholly or partially fill the sprinkler above the plug.   I've seen it.

SL

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Hairfield
Sent: Wednesday, July 13, 2016 9:59 AM
To: [email protected]
Subject: Visual Inspection of CPVC System







We recently had a local AHJ require a visual inspection of a CPVC system prior 
to

doing a hydrostatic test.



All places where a sprinkler head was installed they made us remove the heads 
for the inspection.



Has anyone ever had this happen to them or am I missing something here?



Thanks,



Mike