The drain test is needed if it is downstream of a valve. Every valve needs
exercised, and a flow test needs conducted after the closed valve is
restored to the open position.

On Jul 18, 2016 1:05 PM, "rongreenman ." <rongreen...@gmail.com> wrote:

> John has stated and defended. Mike has stated. Mike, defend your position.
> I'll side with John, using his defense and add that that only one main
> drain test is needed for any lead-in, no matter how many systems and
> auxiliary systems it supplies if all originate from the same header. And,
> as an aside, the test is half useless without having the original test date
> and the latest test data to compare against.
>
> On Mon, Jul 18, 2016 at 9:12 AM, Mike Hairfield <fsl...@msn.com> wrote:
>
>> Yes
>>
>>
>> ------------------------------
>> *From:* Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org>
>> on behalf of Todd Williams <fpdcdes...@gmail.com>
>> *Sent:* Monday, July 18, 2016 11:55 AM
>> *To:* sprinklerforum@lists.firesprinkler.org
>> *Subject:* Auxiliary dry valve drains
>>
>> Are full flow 2" drain tests required for auxiliary dry valves?
>>
>> Todd G Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860-535-2080 (ofc)
>> 860-608-4559 (cell)
>>
>> Sent using CloudMagic
>> <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>
>
> --
> Ron Greenman
>
> 4110 Olson Dr., NW
> Gig Harbor, WA 98335
>
> rongreen...@gmail.com
>
> 253.576.9700
>
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to