Full compliment required above Jerry. The '24ft' thing is under 8.15.23.
Cloud Ceilings is 8.15.24.
Basically you have an exposed system with a lot of obstructions over 48"
wide.

Brad
On Jul 19, 2016 1:52 PM, "Jerry Van Kolken" <[email protected]> wrote:

> I have an building with large cloud ceilings 40’x26’ with 4’ to 6’ gap
> between the clouds and 1’-0” on one side and 3’-0” on the other side to the
> walls. The ceilings are at 13’6” height with a deck height of  18’3”
>
>
>
>
>
> Everything I read from NFPA 13 2016 would require upright sprinklers above
> the ceiling within 24’-0” from the edge of the clouds. I’m I reading this
> correctly?
>
>
>
> This is a 2013 Job.
>
>
>
> Jerry Van Kolken
>
> *Millennium Fire Protection Corp.*
>