Full compliment required above Jerry. The '24ft' thing is under 8.15.23. Cloud Ceilings is 8.15.24. Basically you have an exposed system with a lot of obstructions over 48" wide.
Brad On Jul 19, 2016 1:52 PM, "Jerry Van Kolken" <[email protected]> wrote: > I have an building with large cloud ceilings 40’x26’ with 4’ to 6’ gap > between the clouds and 1’-0” on one side and 3’-0” on the other side to the > walls. The ceilings are at 13’6” height with a deck height of 18’3” > > > > > > Everything I read from NFPA 13 2016 would require upright sprinklers above > the ceiling within 24’-0” from the edge of the clouds. I’m I reading this > correctly? > > > > This is a 2013 Job. > > > > Jerry Van Kolken > > *Millennium Fire Protection Corp.* > > 2950 San Luis Rey Rd. > > Oceanside, CA 92058 > > (760) 722-2722 FX 722-2730 > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > >