“Inside Hose” is generally defined as 3/4 or 1 inch rubber hose that may be 
connected to the sprinkler system for initial fire attack by trained occupants. 
It's should not be confused with standpipe system which is defined in NFPA-14.

US Approach: It is not common to find inside hose stations these days, unless 
the owner requires. Most buildings are not required to have such connections. 
It's not a good idea to install hoses which are usually used by untrained 
occupants. Americans prefer to only use standpipe system for fire department 
that is designed in accordance with NFPA 14, whether it is a Class I system 
with 2-1/2 inch connections or a Class II system with 1-1/2 inch connection or 
a Class III system with both will have its own water supply and its own 
calculations. So no need for inside hose stations!

European Approach: 3/4" hose reels are commonly used in Europe. I think they 
accept 60psi. Why is that? I don't know!

Which approach do you follow in your country and why?

Cheers!

Reza Esmaeili