Plumbing codes do prevail though.  With the possibility of metals, oils, 
anaerobics in suspension, this discharge must go to sanitary.  We put 2x2.5 
NPTxNH adapters on all our testing accounts outlets that exit the building and 
hose to sewer, even 3” drain risers.  Homemade ‘hosemonster’ style diffusers 
suspended down on ratchet straps keep them up and away from the turds and from 
splashing on the street.  Unfortunately inside tight drains, with or without 
sight glasses or air gaps are a thing of the past.  ASPE member since 1979.

TD

 

 

Notwithstanding applicable plumbing codes the sewage authority has restricted 
sanitary to effluent from sinks, water closets, lavatories, dishwashers, 
showers requiring biological treatment, ie grey and black water. The idea is to 
reduce outfall from sources other than above.

 



Jeff Bridges <[email protected] <mailto:[email protected]> > 
wrote:

Technically any discharge into the sewer system would need to be approved, and 
be an Indirect Waste Connection =  1” air gap. The p-trap would also be 
required to have a trap primer also as mentioned earlier.

 

Jeff Bridges JBFP Inc

 