I have a couple questions that pertain to the roles and responsibilities of a 
water-based inspector.

1st Question: Should an inspector inspect water-based systems outside the 
requirements of NFPA 25?  For example, NFPA 25 has no dialogue about 3-way 
shutoff valves for gauges.  However, NFPA 13 (2013) clearly defines the 
requirement of such: 

NFPA 13 (2013) 8.17.3.2    Each gauge connection shall be equipped with a 
shutoff valve and provisions for draining.

Therefore, if a 3-way shutoff valve is missing from installation, does this 
justify a non-compliant tag on the sprinkler riser and correction actions items 
identified to the owner(s)?

2nd Question: If there is a gap between my sprinkler head and the ceiling 
membrane, does this require a non-compliant tag on the riser.   NFPA 101 
outlines this as a smoke partition/barrier issue. NFPA 101 states:

NFPA 101  (2000) - 8.2.4 Smoke Partitions.
8.2.4.1 Where required elsewhere in this Code, smoke partitions shall be 
provided to limit the transfer of smoke. 
8.2.4.2 Smoke partitions shall extend from the floor to the underside of the 
floor or roof deck above, through any concealed spaces, such as those above 
suspended ceilings, and through interstitial structural and technical spaces.
Exception:* Smoke partitions shall be permitted to terminate at the underside 
of a monolithic or suspended ceiling system where the following conditions are 
met:
(a) The ceiling system forms a continuous membrane.
(b) A smoketight joint is provided between the top of the smoke partition and 
the bottom of the suspended ceiling.
(c) The space above the ceiling is not used as a plenum.

 Again, NFPA 25 does not identify this as a deficiency.  Should this be 
justified as non-compliant deficiency?

I do understand the role and responsibility of an inspection does not include 
the design of a water-based systems or of building code.  However, when faced 
with a deficiency from installation (from other codes), should it not be 
identified and corrected under the inspection and testing of a water-based 
system?

I look forward to your feedback and thoughts.

Best Regards,
 
John Allen, CET, CFPS
President



AFS: Allen Fire & Security
Your Safety is Our Success
Direct: 770.715.7261 | Office: 770.723.7280 Ext 2 | Fax: 678.894.4180 
 

  Please consider the environment before printing this email 
This email contains proprietary and confidential material for the sole use of 
the intended recipient and is the sole property of AFS.  Any review, use, 
distribution or disclosure by others without the permission of the sender is 
strictly prohibited. If you are not the intended recipient (or authorized to 
receive for the recipient), please contact the sender by reply email and delete 
all copies of the message.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to