Thanks,

I missed the appendix table.



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *
[email protected]
*Sent:* Monday, September 12, 2016 9:16 AM
*To:* [email protected]
*Subject:* RE: 17/32" in-rack sprinkler



Dewayne,



I believe the table is referring to orifice size, not thread size.  Yes an
8K is 17/32” orifice.



NFPA 13 (2013) Table A.6.2.3.1 outlines orifice size based on K-factor.



Thanks,

Sean VG







*From:* Sprinklerforum [
mailto:[email protected]
<[email protected]>] *On Behalf Of *Dewayne
Martinez
*Sent:* Monday, September 12, 2016 6:59 AM
*To:* [email protected]
*Subject:* 17/32" in-rack sprinkler



When the table calls for ½” in-rack sprinklers at 30psi and 17/32” at 15psi
can I use ¾” k=8.0 for the 17/32”?

Thanks,

Dewayne