In California, we have a code amendment that does NOT allow the design area reduction for QR sprinklers in Ordinary Hazard. However, if you're using the standard unabridged, the area reduction will almost certainly more than make up for the cost difference between sprinklers. If your salon (chemicals, definitely NOT close to Light Hazard, IMHO) or jewelry store has a 10-12' ceiling, you'll get 35-40% reduction and likely save a nominal pipe size all around ...
Steve L. From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Tuesday, September 20, 2016 7:46 AM To: [email protected] Subject: RE: Salon - QR or SR If it's OH SR is fine and probably even cheaper than QR. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com<http://bvssystemsinc.com/> From: Sprinklerforum [mailto:[email protected]] On Behalf Of Ed Kramer Sent: Tuesday, September 20, 2016 10:40 AM To: [email protected]<mailto:[email protected]> Subject: Salon - QR or SR Oh, Wise ones: When designing an OH Gp II area (retail) that's really closer to light hazard (think salon or jewelry store), do the sprinks need to be QR, or is SR acceptable? The easy answer is use QR and be done with it, but selecting an extended coverage sprink gets tricky when trying to satisfy both OH and Light hazard requirements. Thanks, Ed Kramer Bamford Fire Sprinkler