Should Non-Aspirating Sprinkler be listed with a specific foam?  

 

This is what is required by NFPA 409:

 

6.2.2 Deluge Foam-Water Sprinkler System Design and Performance.

 

6.2.2.10 The discharge devices shall have a minimum nominal 6.4 mm (1∕4 in.) 
orifice and shall be listed for use with the particular type of foam 
concentrate to be used in the system.

 

However, such approval is not required by FMGlobal: 

 

FM Global-  Property Loss Prevention Data Sheets 4-12,  Jan 2013

 

3.2 Protection

3.2.1 Where to Find Foam-Water Sprinkler Components in the Approval Guide

The following components are listed in the Foam-Water Sprinkler section of the 
Approval Guide:

• Automatic sprinklers • Deluge sprinklers*

• Aspirated sprinklers • Foam concentrates

* Deluge sprinklers are not listed as such in the Approval Guide; they are 
simply FM Approved automatic

sprinklers that can be ordered in the open orifice (deluge) configuration from 
the manufacturer.

 

I did not find any such requirement in NFPA 11 or NFPA 16 that are more 
specific Standard referenced in NFPA 409.  

 

What is required is to use listed components.  

 

The NFPA 409 requirement as per 6.2.2.10  seems to be rather odd: 

 

It is necessary to use listed components such as sprinklers, accessories and 
Foam. 

 

Aspirating Foam Sprinkler is listed as such without a specific foam. 

 

Why should regular open sprinkler be listed together with a specific foam. 

 

Your comments are welcome. 

 

Dan

 

 

Dan Arbel Risk Engineering