The only issue with the App is that’s it’s not a current edition…..

 

Rocci Cetani III, CET

Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

 <mailto:[email protected]> [email protected]

 <http://www.norcalfire.com/> www.norcalfire.com

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information 

belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ryan Labrie
Sent: Tuesday, September 27, 2016 7:57 AM
To: [email protected]
Subject: RE: Cloud computing for NFPA standards 

 

NFPA also has mobile apps available, I purchased  13-2010 for $10 on my iPhone. 
I prefer the app over searching the PDF because any table or other section is 
linked when referenced. Their selection of single code books is limited but 
they also have an eLibrary app that can access any ebook you have purchased on 
your NFPA account.

 

Ryan Labrie

Fire Protection Designer

 

Critical System Solutions, LLC
2830 Scherer Drive, Suite 300
St. Petersburg, FL  33716
Office: 727.209.5122

Fax:      727.209.5126

Cell:     813.394.3978

Email:  [email protected]

 

CSS Logo

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Tuesday, September 27, 2016 10:48 AM
To: Charles Thurston; [email protected]
Subject: Re: Cloud computing for NFPA standards 

 

Set up a Dropbox account. Put the PDF copies of standards on your Dropbox. Then 
I can access copies of standards right in a meeting or anytime.  

 

It has served me well over the years. 

 

As an outside design firm, embracing cloud computing via the full versions of 
Dropbox has been a game changer. 

 

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:  
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692> 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

 

Sent from my iPhone


On Sep 27, 2016, at 7:42 AM, Charles Thurston <[email protected]> wrote:

Hello Steve,

I have hard copy for my main uses, Carry the PDFs on a thumb drive with me so 
if I really need to find something while I am out, Any computer will let me.

Tuesday, September 27, 2016, 9:41:02 AM, you wrote:



 

 

 

I'm still stubbornly analog and prefer to use the traditional hard copy. This 
is a pretty good reason to take the PDF for a test drive I suppose. 

 

 

 

 

Steve 

 

 

 

 

-------- Original message -------- 

From: Charles Thurston <[email protected]>  

Date: 9/27/16 5:58 AM (GMT-08:00)  

To: [email protected]  

Subject: Re: Question for any member of Installation Sub-TC  

 

 

Hello Tom,

 

I just did a search in the PDF for "Floor Control Valve Assemblies" I came up 
in 8.4.2 as the only location on the whole phrase.

 

Then a search on "Floor Control Valve" came up with : 

8.16.1.1.2.2 Floor control valves in high-rise buildings and

valves controlling flow to sprinklers in circulating closed loop

systems shall comply with 8.16.1.1.2.1(1) or 8.16.1.1.2.1(2).

 

Tuesday, September 27, 2016, 7:53:21 AM, you wrote:

 

 

 

On Sep 26, 2016, at 4:36 PM, Steve Leyton <[email protected]> wrote:

 

That’s my question – has it been rescinded?   Didn’t see it anywhere else in 
the standard but figured it was worth a question …

 

SL

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Joe Burtell

Sent: Monday, September 26, 2016 2:31 PM

To: [email protected]

Subject: Re: Question for any member of Installation Sub-TC

 

2016

 

8.16.1.5* In-Rack Sprinkler System Control Valves.

A.8.16.1.5 In-rack sprinklers and ceiling sprinklers selected for protection 
should be con-

trolled by at least two separate indicating valves and drains. In higher rack 
arrangements, 

consideration should be given to providing more than one in-rack control valve 
in order to 

limit the extent of any single impairment.

 

I would say, yes or it moved?

 

 

Best regards,

 

Joe Burtell, SET, CFPS

 

 

 

<image001.jpg>

 

PH: 406-652-7697

 

Fax: 406-652-7743 | Cell: 406-861-4507

 

Email: [email protected]

 

Web Site: http://www.burtellfire.com

 

NOTICE:  The information contained in this e-mail transmission is intended only 
for use of the individual or entity named above.  This e-mail transmission, and 
any documents, files, previous e-mail transmissions or other information 
attached to it, may contain  confidential information that is legally 
privileged.  If you are not the intended recipient of this e-mail transmission, 
or the employee or agent responsible for delivering it to the intended 
recipient, you are hereby notified that any disclosure, dissemination,  
distribution, copying or other use of this transmission or any of the 
information contained in or attached to this e-mail is strictly prohibited.  If 
you have received this e-mail transmission in error, please immediately notify 
us by return e-mail transmission  and destroy the original e-mail transmission 
as well as its attachments without reading or saving it in any manner.  Thank 
you.

 

 

On Mon, Sep 26, 2016 at 3:17 PM, Steve Leyton <[email protected]> 
wrote:

Was 8.16.1.5 Floor Control Valve Assemblies (13, 2013 edition) completely 
rescinded in 2016 edition?

 

<image002.png>

 

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

 

 

 

 

-- 

Best regards,

 Charles                            mailto:[email protected]

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 




-- 
Best regards,
Charles                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to