> A Quick Response sprinkler does not necessarily activate sooner than a
> standard response sprinkler!
> For example, 155 SRs at 120 S.F. spacing might activate sooner than 155
> QRs at 225 S.F., be they regular pendent or concealers.
>
> We are allowed to use design area reduction when the RTI is 50 (m-s)^2 or
> less and it is listed as quick response, and three other conditions are
> met. The RTI is the physical, non site specific property of the sprinkler,
> and the 'listed as quick response' is the various spacings, ceiling
> heights, etc. tested, with some kind of pass/fail citeria, which i assume
> includes a range of minimum 'real' activation times.
>
> I used 50 and 80 RTI for the QR and SR in the four activation times I
> showed. In more detailed scenarios I have used 38 and 90 based on glass
> bulb manufactures published data. I kind of winged the concealer cover
> plate, but not totally-- I input specific heat, conductivity, and density
> for a dab of solder, and made the plate disappear when the dab reached 135F.
>
> I have been using FDS-SMV for 10 years. For sprinkler activation it is for
> personal curiosity and to try to get a little more insight than I can get
> from NFPA alone.
> I don't try to predict anything, I like looking at 'differences', based on
> RTI, Temp rating, ceiling height, and spacing.
> Fascinating stuff, and I'm glad you brought the 'concealer twist' to my
> activation curiosity Pete!
>
> thanks,
>
> Brad
>
>
> ------------------------------
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Larrimer,
> Peter A
> *Sent:* Tuesday, October 11, 2016 9:18 AM
> *To:* [email protected]
> *Subject:* RE: [EXTERNAL] RE: FM and Concealed Sprinklers
>
> I can’t say I know what you are using for your model, nor how you model
> RTI’s for concealed heads and cover plates, but it sort of begs the
> question.  Why is there a NFPA 13 reduction in design areas for LH and OH
> when the QR concealed head might be slower than a standard response;
> assuming your model results are close to accurate regarding response times.
>
>
> Considering that most fires are controlled with the first one or two
> sprinklers in LH and OH facility fires, maybe the QR vs SR isn’t a big deal
> when it comes to required design areas?
>
> Thanks
> Pete
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to