Mike is right.  However the problem relates to the draining and refill, so
something has changed.  It may be as simple as a check valve that was
holding previously, but is not now.

A possible solution would be to put a time delay relay between the  VS-SP
and the bell. Just a few seconds delay should be satisfactory. You would be
introducing a possible reduction in reliability, however.

On Wed, Oct 12, 2016 at 7:14 AM, Barry Levine <[email protected]> wrote:

> I flushed the system from both the system drain side and the test side.
> The test side is furthest away, while the drain side can be seen in the
> picture by the water inlet. I ran it for a few minutes after all the air
> came out, and nothing has changed.
>
>
>
> On 10/12/2016 6:54 AM, Mark Phillips wrote:
>
>> Open the system drain which is hopefully at the far end of the system
>> while you fill to get air out
>>
>> Sent from my Verizon 4G LTE Droid
>> On Oct 12, 2016 8:38 AM, "Steele, Andrew" <[email protected]>
>> wrote:
>> Check valve failure, so that the sprinkler leg is no longer isolated?
>>
>> -----Original Message-----
>> From: Sprinklerforum [mailto:sprinklerforum-bounces
>> @lists.firesprinkler.org] On Behalf Of Barry Levine
>> Sent: Wednesday, October 12, 2016 1:01 AM
>> To: [email protected]
>> Subject: Seeking false water flow alarm suggestions
>>
>> I drained all the water from my pipes when I installed a new water
>> filter/softener system in my home. After installing the new system, which
>> replaced some 3/4" pipe with 1" pipe in my home water system, I have been
>> getting false alarms from my Potter Electric Signal Co VS-SP flow sensor. I
>> flushed my sprinkler system using the drain and the test valve, yet I
>> believe some air pockets may still remain in my two areas of coffered
>> ceilings, where the sprinklers sit 1 foot above the rest of the system.
>> Potter recommends replacing the VS-SP with a VSR-ST. I'd prefer not
>> spending the money to replace the sensor, but I'd like to hear from the
>> professionals before I make that decision. I'm thinking there may be other
>> solutions, especially since I never had any false alarms during the
>> previous 20+ years. Possibly I could attach saddle valves between each of
>> the two sprinklers in the two coffered ceilings and bleed the air out.
>> Unfortunately, I've never had any long-term luck with sad
>>
> dl
>
>>   e valves, as they have all become inoperative over time. I've attached
>> a photo of my water system in case that might be helpful. Feel free to ask
>> any questions or offer any solutions. Thank you.
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>> iresprinkler.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>> iresprinkler.org
>>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
> iresprinkler.org
>



-- 
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
Cell 925-787-0465
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to