Mike is right. However the problem relates to the draining and refill, so something has changed. It may be as simple as a check valve that was holding previously, but is not now.
A possible solution would be to put a time delay relay between the VS-SP and the bell. Just a few seconds delay should be satisfactory. You would be introducing a possible reduction in reliability, however. On Wed, Oct 12, 2016 at 7:14 AM, Barry Levine <[email protected]> wrote: > I flushed the system from both the system drain side and the test side. > The test side is furthest away, while the drain side can be seen in the > picture by the water inlet. I ran it for a few minutes after all the air > came out, and nothing has changed. > > > > On 10/12/2016 6:54 AM, Mark Phillips wrote: > >> Open the system drain which is hopefully at the far end of the system >> while you fill to get air out >> >> Sent from my Verizon 4G LTE Droid >> On Oct 12, 2016 8:38 AM, "Steele, Andrew" <[email protected]> >> wrote: >> Check valve failure, so that the sprinkler leg is no longer isolated? >> >> -----Original Message----- >> From: Sprinklerforum [mailto:sprinklerforum-bounces >> @lists.firesprinkler.org] On Behalf Of Barry Levine >> Sent: Wednesday, October 12, 2016 1:01 AM >> To: [email protected] >> Subject: Seeking false water flow alarm suggestions >> >> I drained all the water from my pipes when I installed a new water >> filter/softener system in my home. After installing the new system, which >> replaced some 3/4" pipe with 1" pipe in my home water system, I have been >> getting false alarms from my Potter Electric Signal Co VS-SP flow sensor. I >> flushed my sprinkler system using the drain and the test valve, yet I >> believe some air pockets may still remain in my two areas of coffered >> ceilings, where the sprinklers sit 1 foot above the rest of the system. >> Potter recommends replacing the VS-SP with a VSR-ST. I'd prefer not >> spending the money to replace the sensor, but I'd like to hear from the >> professionals before I make that decision. I'm thinking there may be other >> solutions, especially since I never had any false alarms during the >> previous 20+ years. Possibly I could attach saddle valves between each of >> the two sprinklers in the two coffered ceilings and bleed the air out. >> Unfortunately, I've never had any long-term luck with sad >> > dl > >> e valves, as they have all become inoperative over time. I've attached >> a photo of my water system in case that might be helpful. Feel free to ask >> any questions or offer any solutions. Thank you. >> >> >> >> >> >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f >> iresprinkler.org >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f >> iresprinkler.org >> > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f > iresprinkler.org > -- Ed Vining 4819 John Muir Rd Martinez CA 94553 925-228-8792 Cell 925-787-0465
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org