Why is it zoned? Just because it's bigger than 52K? One big open space? Not trying to be a smart ass (or maybe I am) but the FD won't fight a fire in zone 2 that is happening in Zone 1 bec aide an annunciation says here, not there, and it sounds like they'd be able too see the fire on entry.
On Wednesday, October 12, 2016, James Crawford <[email protected]> wrote: > I just came from a building where the in-rack sprinklers are connected > into the adjacent roof system. > > > > The building has two roof zones, north and south, the in-racks are in the > north zone but connected into the south zone (no control valve at the > connection point) > > > > I have never ever thought of doing this as it would send two different > signals in the event of a fire, but cannot seem to find anything that says > you can’t do this, with the exception of alarm signals. > > > > Any comments on this arrangement? > > > > > > Thank you > > > > > > James Crawford > > Phaser Fire Protection Ltd. > > Phone 604-888-0318 > > Fax 604-888-4732 > > Cel 604-790-0938 > > Email [email protected] > <javascript:_e(%7B%7D,'cvml','[email protected]');> > > > -- Sent from Gmail Mobile