When you say "kickers", are you referring to the braces at 45° that hold up a roof feature (parapet/mansard)? Is there sheathing over these kickers and does it create a combustible concealed space above the structural roof diaphragm that's deeper than 6" clear and otherwise doesn't meet the volume exceptions? If all that is in place, you have to sprinkler these cricket spaces.
Steve L. From: Sprinklerforum [mailto:[email protected]] On Behalf Of Steve Sorrell Sent: Tuesday, November 08, 2016 7:27 AM To: [email protected] Subject: Roof Parapet Protection I have an architect that is insisting that the space above the roof line caused by the kickers supporting the parapet walls needs to be sprinkled. Has anyone had any experience with this ? Stephen J. Sorrell, CET NICET# 77901 Level III E mail: [email protected]<mailto:[email protected]> Senior Designer Performance Fire Protection, LLC Corporate Office 179 Gasoline Alley - PO Box 4510 Mooresville, NC 28117 Phone: 704-663-1664 Fax: 704-663-1652 Cell : 704-309-1242 Web: www.performancefire.com<http://www.performancefire.com/> Licensed in NC, SC, VA, TN, GA, AL "Performance on Every Level."