When you say "kickers", are you referring to the braces at 45° that hold up a 
roof feature (parapet/mansard)?   Is there sheathing over these kickers and 
does it create a combustible concealed space above the structural roof 
diaphragm that's deeper than 6" clear and otherwise doesn't meet the volume 
exceptions?  If all that is in place, you have to sprinkler these cricket 
spaces.

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Sorrell
Sent: Tuesday, November 08, 2016 7:27 AM
To: [email protected]
Subject: Roof Parapet Protection

I have an architect that is insisting that the space above the roof line caused 
by the kickers supporting the parapet walls needs to be sprinkled.
Has anyone had any experience with this ?