One assumes this is a light hazard occupancy, in which case when the sprinklers 
are changed they can (and probably should) be changed to QR per 8.3.3.4 (NFPA 
13 2013),  NFPA 25 also exempts response characteristics from the items that 
must be the “same” in replacement sprinklers in A.5.4.1.4 in NFPA 25 2014.

On Nov 26, 2016, at 12:25 AM, Douglas Hicks 
<[email protected]<mailto:[email protected]>> wrote:

We have a child care in the basement of a church, fully wet sprinkled (except 
for a couple of closets).  When we first did the service a couple of years ago, 
I noted the sprinkler heads in the basement were getting close to 50 years old, 
and they should think about budgeting for the replacement/testing. So, a 
competitor got the job.  All the SR fusible heads replaced were replaced with 
QR heads.   I thought we were to use the same type of replacement heads, as 
were originally installed.  Am I wrong?