Here if you add one head at all you calculate.
If you relocate any head more than five feet total including break over and 
drop you calculate.
If the existing facility has a pump. You need a current a certified pump by a 
manufacturer rep or sealed by a PE
And you need to take it the street tie in with a current flow test performed by 
a AHJ certified tester and witnessed by the city.

We figure calculating every job so no matter what size job it's going to be 
2500 out of the gate.
But it's the standard so everyone is equal.

That is as long as you read the city requirements for permitting.


Sent from my Verizon 4G LTE Droid
On Dec 15, 2016 6:12 PM, "Travis Mack, SET" <[email protected]> wrote:
How many of you are having to provide calculations when you do a tenant
remodel?  I'm not talking about changing densities or even going from
standard to extended coverage sprinklers.  I just mean your average run
of the mill add/relo project.

We have run into a fire marshal that feels it is required on all
projects now.  The one that they are currently fighting is just a tenant
change in a strip mall.  Building has been around for nearly 30 years.
Water supply in area is very stable.  Would you normally figure a full
calculation on this type of project?


--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to