Ron-
You want my address?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Thursday, January 12, 2017 10:43 AM
To: [email protected]
Subject: Re: Funky Wavy Soffit

I think that whenever someone posts a reference number and doesn't include the 
text or at least the edition he should be severely beaten.

On Thu, Jan 12, 2017 at 6:24 AM, Brian Harris 
<[email protected]<mailto:[email protected]>> wrote:
We have a grocery store that has a wavy kinda soffit (see dropbox file link 
below) around the perimeter of most of the store. The top of this soffit is 
approximately 5’0” below the overhead sprinklers & is less than 48” at the 
widest points. With that being said are additional heads needed in this lower 
soffit? In my opinion 8.6.5.2 would not apply since the pattern development is 
not affected so the next stop would be 8.6.5.3. The only thing that stands out 
to me there would be the 48” width we I do not have. So I say no additional 
heads needed below, what say you?

https://www.dropbox.com/s/3klcgh37fhowmp8/Wavy%20Soffit.pdf?dl=0

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989<tel:(704)%20896-9989>
Fax: 704.896.1935<tel:(704)%20896-1935>


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Ron Greenman

[email protected]<mailto:[email protected]>

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to