Subject: QR STANDARD SPRAY SPRINKLERS

 

I KNOW FOR 13R YOU NEED TO BE A MINIMUM OF 3'-0" AWAY FROM THE CENTER OF A
CEILING FAN WITH RESIDENTIAL HEADS

 

I CANNOT FIND WHERE THE SAME APPLIES FOR A 13 SYSTEM USING STANDARD Q.R.
PENDENT OR CONCEALED HEADS.

 

CAN SOMEONE VERIFY OR EDUCATED ME ON THIS PLEASE?

 

THANKS


2013 NFPA 13 - 8.6.5.2.1.10 specifically addresses ceiling fans; "Sprinklers
shall be permitted to be placed without regard to the blades of ceiling fans
less than 60 in. in diameter, provided the plan view of the fan is at least
50 percent open." As others have noted, A8.6.5.2.1.10 states that the
housing of the fan is expected to be addressed by the Three Times Rule. The
Handbook has further explanatory material which states that this only
applies to light hazard occupancies 

George Gray
Northeast Fire Protection
350 Sargent Road
Gilmanton, NH 03237

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Tuesday, January 24, 2017 8:43 AM
To: [email protected]
Subject: Sprinklerforum Digest, Vol 46, Issue 31

Send Sprinklerforum mailing list submissions to
        [email protected]

To subscribe or unsubscribe via the World Wide Web, visit
        
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

or, via email, send a message with subject or body 'help' to
        [email protected]

You can reach the person managing the list at
        [email protected]

When replying, please edit your Subject line so it is more specific than
"Re: Contents of Sprinklerforum digest..."


Today's Topics:

   1. RE: QR STANDARD SPRAY SPRINKLERS
      (Trillium Fire Sprinkler Design Inc.)
   2. RE: QR STANDARD SPRAY SPRINKLERS (Bob)
   3. Re: QR STANDARD SPRAY SPRINKLERS (Travis Mack, SET)
   4. RE: QR STANDARD SPRAY SPRINKLERS (Bob)
   5. RE: QR STANDARD SPRAY SPRINKLERS (Mark Phillips)
   6. Re: PIV Supervion, lock or tamper switch? ([email protected])
   7. Re: Ammunition Manufacturer (Roland Huggins)
   8. Re: Ammunition Manufacturer (Brad Casterline)
   9. Re: PIV Supervisor, lock or tamper switch? ([email protected])
  10. RE: PIV Supervisor, lock or tamper switch? (Steve Leyton)
  11. RE: Ammunition Manufacturer ([email protected])



------------------------------

End of Sprinklerforum Digest, Vol 46, Issue 31
**********************************************

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to