The first thing you have to do is find listed anti-freeze.  Good luck.  The 
rest is mood point if you are following the 2013 or newer NFPA 13 (7.6.2)

Duane T. Fox, Jr., CFPS, CFI, CFPE
Asst Chief, Technical Services
DE State Fire Marshal’s Office
302-856-5298



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dale Wingard
Sent: Monday, January 30, 2017 9:44 AM
To: [email protected]
Subject: Re: Check valves on Antifreeze loops

First, the loop requires a Reduced Pressure Backflow.  Are you using the check 
valves to separate the two canopies?

Sent from my Verizon Wireless 4G LTE DROID


Douglas Hicks <[email protected]<mailto:[email protected]>> wrote:
We have a building with 2 outside canopies, each is protected by an antifreeze 
loop.  The sprinkler system has a backflow in a pit.  Do each of  the 2 
antifreeze loops need a one way swing check valve, with a hole in the clapper? 
I will put a test port at each end of both loops, even though the loops are not 
150 gallons.