Travis,

There is a section in the appendix which shows milk going from a Class I to
Group A plastic with the addition of plastic crates.  Maybe that’s where
you saw it.



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *Roland
Huggins
*Sent:* Monday, February 13, 2017 11:34 AM
*To:* SprinklerFORUM
*Subject:* Re: Commodity class upgrade?



There is guidance in the annex about when the definition of Class IV for
the allowed amount of plastics does not apply.  That being location within
the load.  Look at A.5.6.1.1 and Table A.5.6.3 (2013 edition) for plastic
jars  and more specifically Plastic Crates and note C.  Note C points out
that openings in the crates reduces the classification (using the
non-quantified statement of - as the openings become larger).





Roland Huggins, PE - Senior VP Engineering

American Fire Sprinkler Assn.

Dallas, TX

http://www.firesprinkler.org



Fire Sprinklers Saves Lives









On Feb 11, 2017, at 11:33 AM, Travis Mack <[email protected]> wrote:



I have a project where they are storing class III commodities in plastic
totes. The product is stored on racks with 12' to top of storage.



Does the plastic totes cause me to increase / modify the commodity class? I
swear I read something about that in the storage chapters but I can't seem
to locate it. This jurisdiction is under the 2013 edition of NFPA 13.



Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign



Sent from my iPhone

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to