Mike,

 

1) Need to know the min. and max. ambient air temperatures.

 

2) May I contact you off Forum?

 

Brad

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mike Stossel
Sent: Tuesday, February 28, 2017 7:17 AM
To: [email protected]
Subject: Air Relief Time

 

I am trying to calculate the time it will take for a 2-1/2" hose valve to
relieve a standpipe system of air.  I am designing a temporary standpipe
system in NYC and the requirement is to fill the entire system with air and
a single 2-1/2" hose valve needs to relieve the pressure within 3 minutes or
a second will need to be added.  My total system volume will be 1902 gallons
and the staring air pressure will be at 18psi.  Does anyone know of a way to
calculate this?

 

Thanks for the help.

 

Mike Stossel SET