All, I was asking the question based on information given me by one of my trainee designers (I was also showing him how to use the forum since I'm not always going to be around). Dug into it a little further and I think we have solved the problem.
As far as the crown molding is concerned, it a basically an reverse ogee molding installed on the face of the cabinet, sticks out 2" and is 2" down on the face of the cabinet, sort of like this |/. | And in reality the head would be almost 6' above the top of the cabinet in this scenario. Viking makes a Residential sprinkler that works well for spraying down the slope, which is what this installation would require. http://www.vikingcorp.com/vk486-residential-horizontal-sidewall-sprinkler-k40 Richard Mote Design Manager [http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg] P: 570.837.7647 * W: 877.324.ROWE * F: 570.837.6335 PO Box 407 * 7993 US Route 522, Suite 1 * Middleburg, PA 17842 RoweSprinkler.com * rich...@rowesprinkler.com<mailto:rich...@rowesprinkler.com> *** Confidentiality Notice *** This email and any attachments thereto may contain information that is privileged and confidential and is intended only for the use of the addressee. If the reader of the message is not the intended recipient or an authorized representative of the intended recipient, you are hereby notified that any dissemination of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by e-mail at rich...@rowesprinkler.com or by telephone at 570-837-7647 and delete the message and any attachments permanently from your system. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brian Harris Sent: Tuesday, March 07, 2017 11:22 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Cabinets Against a Wall Semantics..... :) Brian Harris, CET BVS Systems Inc. bvssytemsinc.com<http://bvssystemsinc.com/> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack, SET Sent: Tuesday, March 07, 2017 11:21 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: Re: Cabinets Against a Wall Yes, but that is considered flat for NFPA purposes so there is no up or down slope in a "flat" ceiling :-) Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com> http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign LinkedIn: https://www.linkedin.com/in/travismack On 3/7/2017 9:19 AM, Brian Harris wrote: If memory serves me correctly you can slope uphill if the pitch does not exceed 2:12 Brian Harris, CET BVS Systems Inc. bvssytemsinc.com<http://bvssystemsinc.com/> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack, SET Sent: Tuesday, March 07, 2017 11:18 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: Re: Cabinets Against a Wall I always thought it was cross slope and down, but never up. Has that changed? Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com> http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign LinkedIn: https://www.linkedin.com/in/travismack On 3/7/2017 9:17 AM, Steve Leyton wrote: I didn't get that impression at all, so perhaps it's still a little too obscure. Is it the intent that residential sidewalls can be arranged so they discharge cross-slope and up-slope? I don't think so ... SML From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Matt Grise Sent: Tuesday, March 07, 2017 8:11 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Cabinets Against a Wall Steve, I got the impression NFPA13d 2016 8.1.1 was meant to deal with both pendant and sidewall sprinklers. The picture shows only pendants, but it is in a section separate from the pendant/sidewall positioning sections. Section 10.2 also makes several references to general and sidewall spacing under slopes. Also - the tyco listings previously had multiple diagrams showing how to position residential sidewalls under sloped ceilings. Those were removed after the 13R/D code language was changed to the generalized description of heads under slopes. Matt From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve Leyton Sent: Tuesday, March 07, 2017 9:44 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Cabinets Against a Wall Sloped ceiling? Can a sidewall be oriented so it discharges down-slope? You comment sent me scurrying to our tech data library and also to NFPA 13D and 13. Both standards are mute regarding the positioning of residential horizontal sidewall sprinklers on/under sloped ceilings. Viking tech data sheets say to refer to the appropriate standard. Tyco says their RHSW sprinklers can be used under sloped ceilings but no specific positioning criteria is offered. If we use the spray sprinkler criteria, the sprinklers have to be oriented so they are placed at the peak of a sloped ceiling and spray downward. Am I missing something somewhere regarding RHSW sprinklers and sloped ceilings? Steve L. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Richard Mote Sent: Tuesday, March 07, 2017 6:18 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Cabinets Against a Wall This a sloped ceiling area, with the ceiling being attached directly to the underside of the joists. No space to run pendants in a conditioned area. Richard Mote Design Manager [http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg] P: 570.837.7647 * W: 877.324.ROWE * F: 570.837.6335 PO Box 407 * 7993 US Route 522, Suite 1 * Middleburg, PA 17842 RoweSprinkler.com * rich...@rowesprinkler.com<mailto:rich...@rowesprinkler.com> *** Confidentiality Notice *** This email and any attachments thereto may contain information that is privileged and confidential and is intended only for the use of the addressee. If the reader of the message is not the intended recipient or an authorized representative of the intended recipient, you are hereby notified that any dissemination of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by e-mail at rich...@rowesprinkler.com<mailto:rich...@rowesprinkler.com> or by telephone at 570-837-7647 and delete the message and any attachments permanently from your system. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Matt Grise Sent: Tuesday, March 07, 2017 8:56 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Cabinets Against a Wall Pendant sprinkler? Matt From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Richard Mote Sent: Tuesday, March 07, 2017 7:50 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: Cabinets Against a Wall NFPA 13D, 2017 (the edition currently in force in PA) 8.2.5.6.3 Where sidewall sprinklers are more than 3 ft. above the top of cabinets, the sprinkler shall be permitted to be installed on the wall above the cabinets where the cabinets are no greater than 12 in. from the wall. We have a case that meets all of the above criteria except for a 2" wide crown molding around the top of the cabinets, so the overall width is 14" around the top of the cabinet. Obvious solution is put the sprinkler on the other end of the room, however that wall is a rated wall with a un-conditioned space on the other side. Any sugestions? Richard Mote Design Manager [http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg] P: 570.837.7647 * W: 877.324.ROWE * F: 570.837.6335 PO Box 407 * 7993 US Route 522, Suite 1 * Middleburg, PA 17842 RoweSprinkler.com * rich...@rowesprinkler.com<mailto:rich...@rowesprinkler.com> *** Confidentiality Notice *** This email and any attachments thereto may contain information that is privileged and confidential and is intended only for the use of the addressee. If the reader of the message is not the intended recipient or an authorized representative of the intended recipient, you are hereby notified that any dissemination of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by e-mail at rich...@rowesprinkler.com<mailto:rich...@rowesprinkler.com> or by telephone at 570-837-7647 and delete the message and any attachments permanently from your system. _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org