I'd be more concerned with failure to drain than failure to close during fire. 
Hook up a couple lines, pump for 150 psi at the FDC. A little water out the 
ball drip should not change the outcome.

Bruce Verhei 

> On Mar 30, 2017, at 21:16, IPA <[email protected]> wrote:
> 
> The ones from Viking are rated to 250 psi. I would imagine a ball drip 
> failure is practically impossible.
> 
> 
>> On Thu, Mar 30, 2017 at 9:00 AM, AKS-Gmail-IMAP <[email protected]> wrote:
>> The question brings up another question. The fine print disclaimer on most 
>> of the ball drip cut sheets for ball drips sold for FDC application say the 
>> unit is rated for a ridiculously lower pressure than what one would expect 
>> when the FDC is in use. I’ve asked manufacturer’s reps to explain exactly 
>> the implications for the disclaimers. The best answer I got was, “We don’t 
>> know but the ball inside is SS.” I could make a number of guesses, but that 
>> is not knowing the real skinny.
>> 
>> Allan Seidel
>> St. Louis, MO 
>> 
>>>> On Mar 29, 2017, at 8:21 AM, Hinson, Ryan <[email protected]> wrote:
>>>> 
>>> 
>>>> Can the ball drip actually be verified
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org