This can be a difficult one to navigate. The starting point for most
jurisdictions are the I-Codes and 2015 IFC section 903.3.1.1 in particular.
If the building is being sprinklered to NFPA 13, 903.3.1.1 requires
"sprinklers to be installed throughout", with the exceptions of
903.3.1.1-.2.  Item 4 of 903.3.1.1.1 exempts "rooms or areas that are of
noncombustible construction with wholly noncombustible contents". IFC says
no combustibles- NFPA recognizes "limited" combustible construction "fire
retardant-treated wood", materials not exceeding 1000 Btu/ft2, etc . Every
office building will have some combustible insulated wiring, etc. in the
space. Most AHJ's won't get too concerned, as it's not enough combustibles
to warrant protection- that is until then they walk in one day and there are
low voltage cable bundles/trays above the ceiling (like above a hospital
exit corridor I encountered). It's worth asking some questions and getting
the AHJ's concurrence.

 

Travis E. Allen, PE

Allen Engineering, PLLC

 

On 4/3/2017 12:37 PM, Brian Harris wrote:

Are you talking A8.15.1.2.16 (2013) since there's heads above in the attic?

 

Brian Harris, CET

BVS Systems Inc.

bvssytemsinc.com <http://bvssystemsinc.com/> 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Travis Mack, SET
Sent: Monday, April 03, 2017 3:35 PM
To: [email protected]
Subject: Re: Concealed Space / Office Debate

 

That is very similar to one of the diagrams in NFPA 13 that shows you do not
need 3 levels of sprinklers.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
 
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign 
LinkedIn: https://www.linkedin.com/in/travismack

On 4/3/2017 12:32 PM, Brian Harris wrote:

There's a debate in house about whether the space above a drop ceiling and
the drywall attached to wood joist above in an all wood building requires
protection (please see link below).

What say the forum?

 

https://www.dropbox.com/s/6ltbo57nmi4wh7p/Concealed%20Space.pdf?dl=0

 

Brian Harris, CET

BVS Systems Inc.

Design Manager

bvssystemsinc.com <http://bvssystemsinc.com/> 

Phone: 704.896.9989

Fax: 704.896.1935

 






_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to