I'd spend more time making sure adequate length was in the heated portion.
Best Bruce Verhei > On Apr 13, 2017, at 05:19, Richard Carr <[email protected]> wrote: > > I have seen it done many times and could not find a good reason why it would > not protect a small area. > > Richard Carr, SET > Branch Manager > Cox Fire Protection, Inc > 6555 Grace Lane. > Jacksonville, Fl. 32205 > [email protected] > 904-781-8227 > > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Zachary Siegrist > Sent: Thursday, April 13, 2017 8:17 AM > To: [email protected] > Subject: Exterior projection 45 degree angle figure 8.15.7 > > I have a contractor submitting a detail to protect unheated storage closets > off the balcony ( minimal in size) with a dry pendant extending > down at a 45 degree angle as shown in figure 8.15.7 in the 2013 edition. My > take is that this section applies to exterior projections including roofs, > canopies, balconies, and other like projections and this section does not > apply to a room. Thoughts? > > Zach > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org