I would disagree with this unless you can direct me to some more information. 
8.15.7.3(2) even goes on to spell out Light and Ordinary Hazard Occupancy 
situations where sprinklers can be omitted.

John Irwin - CET
Division Manager - Fire Sprinklers
Critical System Solutions, LLC
Licence Number: FPC16-000053
Cell:     813.618.2781
Email:  
[email protected]<mailto:[email protected]>

[cid:[email protected]]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Monday, April 17, 2017 8:53 AM
To: [email protected]
Subject: RE: Covered Restaurant Seating Area

Overhang exceptions only apply when the area below is not used for storage or 
handling of combustibles or otherwise classified as occupied by the applicable 
building code or building official. As Spicey would say, restaurant seating 
areas are assembly occupancy, PERIOD!


Steve


-------- Original message --------
From: John Irwin 
<[email protected]<mailto:[email protected]>>
Date: 4/17/17 5:45 AM (GMT-08:00)
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Covered Restaurant Seating Area

I'm using 13 8.15.7 to argue that if the fabric covering the steel frame is 
non-combustible than perhaps the sprinklers are not required.

[cid:[email protected]]

John Irwin - CET
Division Manager - Fire Sprinklers
Critical System Solutions, LLC
Licence Number: FPC16-000053
Cell:     813.618.2781
Email:  
[email protected]<mailto:[email protected]>

[cid:[email protected]]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Monday, April 17, 2017 8:33 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Covered Restaurant Seating Area

Often, we try to read the standards backwards. The way that NFPA 13 is written, 
it requires sprinklers everywhere. What the client is hopeful of is an 
exception but I'm pretty sure they are not going to find one for this 
particular application.  If I'm taking the contrary point of view, I would say 
that instead of looking for a section  that requires sprinklers here or there,  
show me where it says I don't have to put sprinklers over this occupied area 
that is part of the use of the protected premises.


Steve Leyton




-------- Original message --------
From: John Irwin 
<[email protected]<mailto:[email protected]>>
Date: 4/17/17 4:11 AM (GMT-08:00)
To: 
[email protected]<mailto:[email protected]>
Subject: Covered Restaurant Seating Area

Here's the situation. Existing restaurant seating area covered by steel frame 
and vinyl or nylon tarp. 100% open. Protected with sprinklers.

Additional covered seating area being added that will be steel frame but 
insulated aluminum panel roof. 100% open.

Client doesn't believe sprinklers are required and wants the existing 
sprinklers under the vinyl canopy removed.

Can someone direct me to code references?


John Irwin
Division Manager - Fire Sprinklers
Critical System Solutions, LLC
License Number: FPC16-000053
2830 Scherer Drive, Suite 300
St. Petersburg, FL  33716
Office: 727.209.5122
Fax:      727.209.5126
Cell:     813.618.2781
Email:  
[email protected]<mailto:[email protected]>



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to