We are providing  in-rack protection for a customer who has a combustible 
liquids room they are protecting in accordance with Scheme A (NFPA #30 2012 ed. 
section 16.6) When I received their final rack layout, it contains a section on 
the end of every rack (both single and double) that are only 6'-0" in length.  
(For information sake, the racks are 4'-0" in width and the aisles are 12' 
apart) As I view figures 16.6.1.1(a) and 16.6.1.1(b) it seems pretty clear that 
the transverse flues are required to be a minimum of 8'-0" apart. The owner is 
frustrated, because of the space they will lose if they can't have any racks 
less than 8'-0".  Does anyone know the reason the racks can't be less than 8'0 
in length, or at least some way I can explain it to the customer outside of," 
that's just what code says."?

 

 