I have a pump room where an esteemed colleague suggested I locate the fire pump 
test header control valve near the test header on the vertical pipe to limit 
the amount of “dry” pipe.  Since the valve would be located near the top of 
vertical pipe the dry portion of the pipe would drain well and wouldn’t have 
corrosion issues.  However, NFPA 20 says that the valve “shall be at a point in 
the line close to the pump.”  (NFPA 20, 2013 ed. 4.20.3.3.3).  I know the valve 
needs to be at least 4’ from the exterior wall along the pipe for freeze 
issues, but does anyone know the reason 20 requires that valve be close to the 
pump?

Thanks.