Victaulic style 707C or the NIBCO equivalent must be used. I do not believe any 
other manufacturers make a Listed normally closed monitored butterfly valve. 
This is a NFPA 20 requirement.

John

John August Denhardt, P.E.
Strickland Fire Protection

On Jun 22, 2017, at 2:34 PM, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:

Are you asking about valves that are described in a tech data sheet as a 
“normally closed butterfly valve”?   Like in Nibco’s catalogue, you have to 
order the N suffix or something like that?  Assuming yes, all that means is 
that it’s a regular, everyday fire protection butterfly valve but the tamper 
switch kit is factory-wired for NC service.   So if your question is about the 
tamper switch, yes you want normally closed ones for a flow meter/test bypass.

I think.

SL

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark Phillips
Sent: Thursday, June 22, 2017 11:16 AM
To: 
'[email protected]<mailto:[email protected]>'
Subject: Fire pump flow meter butterfly valves

I keep going back and forth on the answer so I am asking for help

Does the flowmeter bypass butterfly valves have to be normally closed monitored 
valves? Or can they be just be monitored butterfly valves.
Thanks in advance


Mark