I have always found 8" centerline above finished ceiling to work well.  This 
usually keeps us below the bulk of the ductwork but high enough that the lights 
can be installed as long as the sprinkler pipe is not run over the center of 
the light fixture.  You must avoid can lights, but otherwise it works out well. 
 Of course, each project is different so it doesn't always work, but this is my 
ideal setup.


Seismic bracing will change this.  If there is a lot of space between the 
ceiling and the structure, I will run the pipe at the structure to make the 
bracing work out better and drop to the heads.


Just my two cents.  I'm sure others have a different perspective, but this has 
worked out well in many different types of projects with and without BIM 
coordination.

________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Joseph Meyer <[email protected]>
Sent: Monday, June 26, 2017 10:35 AM
To: [email protected]
Subject: Pipe Height Above Ceiling

What is your preferred (ideal) height to run sprinkler pipe above suspended 
ceilings?

Is your preference to run as low as possible above the depth of the lights to 
save on pipe, to run a fixed height above the ceiling (ie: 8", 12", 14") to 
simplify cut lengths, just run anywhere in between the lights and ductwork, or 
something else? I've heard a few different approaches to this question and was 
curious what considerations our experts here make when determining how high to 
run.

Thanks in advance.

--

Joseph Meyer, P.E.
Fire Protection Engineer
[SSC         Engineering]
18207 Edison Avenue
Chesterfield, MO 63005
Phone: (636) 530-7770 x 149
Fax: (636) 530-7877
[email protected]<mailto:[email protected]>

SSC is now providing FULLY ENGINEERED Fire Protection services
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to