Owen,

First, per NFPA 72 a tamper switch is defined as a supervisory signal-initiating device in chapter 17.16 [2013]. It functions when a switch is closed, completing a circuit. In this respect it is no different than a smoke detector as the alarm signal, in this case supervisory, is only created when the valve is moved two or fewer revolutions of the hand wheel of the valve or upon motion of the control apparatus of the valve of more than 1/5th of its travel distance.

As for how many of these devices can be supplied by one pair of wires that answer is only limited by NFPA 72, which limits the number of such devices on a circuit. Section 23.8.5.6.2 [2013] advises that:

   The number of supervisory signal–initiating devices permitted to be
   connected to a single initiating device circuit shall not exceed 20.

There may be limitations established by the device manufacturer, or the panel, or the addressable modules and the listing of those devices should be reviewed prior to raising an alarm [no pun intended].

Further, the explanatory text in the handbook gives the following information [all emphasis is mine]:

   The Code permits up to 20 supervisory signal–initiating devices on
   a_*single initiating device circuit*_ because doing so does not
   degrade the reliability or operability of the fire alarm system. Site
   specific needs and conditions might dictate that a circuit serves
   fewer devices. For example, if a facility has 20 sprinkler control
   valves each equipped with a supervisory switch, _*all the valve
   supervisory switches could be connected to the same initiating
   device circuit and still comply with the Code*_. However, if a
   supervisory signal were received, it would require that someone
   check every valve to find the one initiating the signal. Supervisory
   signal–initiating devices include valve supervisory switches, air
   pressure switches, building temperature switches, fire protection
   water tank level and temperature switches, and other devices that
   are designed to ensure that fire protection and life safety features
   are in service at the time of a fire. Refer to the defined terms
   supervisory signal-initiating device and supervisory signal in
   3.3.132.5 and 3.3.257.9.

So, there doesn't appear to be any reason that such an arrangement as you've described would not be in compliance with the applicable code. You might also ask for testing to prove that the tampers on all of the valves generate the required signal at the panel.

sincerely,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 07/04/2017 9:38 AM, [email protected] wrote:
Here is the situation on an installation at a new hotel. The DCVA has tamper 
switches. Two PIV's near by do not have tamper switches. The hotel is complete, 
no wiring had been run to the PIV's. (CFC 903.4) The DCVA and PIV's sit within 
the same large planter with lots of finished concrete between the valves and 
the alarm panel, about 150'. So the alarm guys tapped into the wiring of the 
DCVA tampers and ran it to the PIV's to install tampers. Is that legal? If a 
PIV is closed will it show at the panel or monitoring company as a DCVA tamper? 
I'm not knowledgeable on the wiring of devices.
Owen Evans
13D Design

Sent from my iPhone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to